Parker 890 drive HOT fault.

We have 3 Parker 890 drives (Model: 890SD-532450D0-B00-1A000) installed in one of our machines. Every year at least one of these three drives fail with HOT fault. The fault doesn't get reset even if the drive is in off condition for months. Once the drive fails with HOT fault, the heat sink temperature in drive's display starts showing constant 125°C, even if the ambient temperature of the panel remains between 28-32°C and there is enough gap between all three drives. 

For repairing the drive we replaced old PCB (AH500819U001/1   AH500819T011/1) by installing newly purchased PCB (AH500819U001 04). But after installing new PCB the drive starts tripping with fault "INCOMPATIBLE STO TEST RECORD".

Please suggest why our drives are regularly failing with "HOT" fault. And also suggest the part no. of spares or PCBs to be replaced in order to repair the drive.

Parents
  • Hello electrical@nuhasoman.com.  

    I will need to check with one of the design engineers regarding the board numbers you reference.  In general, if the "Incompatible STO Test Record" alarm occurs the drive needs to come on an RMA for repair/correction.  However, I can also check with design on that.  Are you using the STO inputs/features or simply jumpering them defeated?

    I will run the questions on the repair parts and STO alarm by a design engineer in the morning and post a follow up.

    In terms of the HOT alarm, your description implies a hard circuit failure or something damaged in teh assembly, leading the fault circuit to mis-read the heat sink temperature, thus no matter how long you let it sit (typically 30-45 minutes is plenty of time for a unit to cool back down to ambient all things considered) it shows that HOT fault immediately and seems to mis-read the temperature.  

    1.  Are the drives installed in an enclosure?

    2.  Is the enclosure ventilated?

    3.  Where are you located?

Reply
  • Hello electrical@nuhasoman.com.  

    I will need to check with one of the design engineers regarding the board numbers you reference.  In general, if the "Incompatible STO Test Record" alarm occurs the drive needs to come on an RMA for repair/correction.  However, I can also check with design on that.  Are you using the STO inputs/features or simply jumpering them defeated?

    I will run the questions on the repair parts and STO alarm by a design engineer in the morning and post a follow up.

    In terms of the HOT alarm, your description implies a hard circuit failure or something damaged in teh assembly, leading the fault circuit to mis-read the heat sink temperature, thus no matter how long you let it sit (typically 30-45 minutes is plenty of time for a unit to cool back down to ambient all things considered) it shows that HOT fault immediately and seems to mis-read the temperature.  

    1.  Are the drives installed in an enclosure?

    2.  Is the enclosure ventilated?

    3.  Where are you located?