DC Integrator 590+ Burnt Components on Main Board

Hello everyone,

A client of mine has a 590+ Series 2 Frame 2 DC Integrator that has performed successfully in a PPR pipe extruder machine for a number of years without any issues. 

A few weeks ago, I was informed that the motor controlled by the drive stopped working and the drive displayed "Field Failed.  On checking, I found the listed components burnt on the main board.

These components are marked In red in the first attached picture. All burnt components are shown in the second attached picture.

1. Controlled Bridge Rectifier - VGO36-16io7 - shorted gates to cathodes of thyristor.

2. The 2 0.033uF PME  261 capacitors on lower part of the board 

3. The 4 47nF PME 271 capacitors on the lower part of the board.

4. The 3 27 Ohms resistors on the lower part of the board.

All burnt components were replaced and the drive reinstalled. However, on powering up the machine, the drive displayed "Field Failed" alarm. On checking field rectifier module, I found its thyristor gates are shorted to the cathodes.

Please note that the drive's parameters were not altered.

Could anyone please suggest the possible cause of the failure of the components and what the solution is.

Many thanks.

Henry

Parents
  • It looks like the field circuit took a hit, destroying the field bridge and associated R-C snubbers.

    I would get the motor meggered and checked for shorts between the field and armature windings and field to ground.

     

    If the motor checks out OK, then we need to determine how a higher voltage may have got into the field circuit.

     

    Is this drive powered from an isolation transformer or 3% line reactor in the supply? If not, one of them need to be added.

    William

Reply
  • It looks like the field circuit took a hit, destroying the field bridge and associated R-C snubbers.

    I would get the motor meggered and checked for shorts between the field and armature windings and field to ground.

     

    If the motor checks out OK, then we need to determine how a higher voltage may have got into the field circuit.

     

    Is this drive powered from an isolation transformer or 3% line reactor in the supply? If not, one of them need to be added.