convertir variador 590G a 591G

Existe un procedimiento para configurar un variador regenerativo de 4 cuadrantes y no regenerativo de 2 cuadrantes.tendrtendria una limitacion en la corriente de armadura .

Parents
  • All you need to do is set the REGEN ENABLE parameter to 2Q (NON-REGEN).  You can do this in DSE Lite on the Current Loop block.  You can also change this parameter from the keypad under SETUP PARAMETERS > CURRENT LOOP > REGEN ENABLE.  Also, it is a good idea to connect terminal A5 (negative current clamp) to A1 (ground).

Reply
  • All you need to do is set the REGEN ENABLE parameter to 2Q (NON-REGEN).  You can do this in DSE Lite on the Current Loop block.  You can also change this parameter from the keypad under SETUP PARAMETERS > CURRENT LOOP > REGEN ENABLE.  Also, it is a good idea to connect terminal A5 (negative current clamp) to A1 (ground).