Parker 890 drive replacement by Parker AC30

I have 3 Parker 890 Drives installed in a machine. 1st drive communicates with S7-300 PLC through Profibus communication and at the same time all three drives communicate to each other through firewire. Can I replace Parker 890 drives with AC30P or AC30D series drives. Can AC30 drive communicate to AC890 over firewire?

Parents
  • Ravi,

    The AC30 line does not support the firewire protocol.  For the AC30's in North America, we usually recommend LinkNET as the peer-to-peer communication between the drives.  There should not be any programming difference when using LinkNET, but there may be other differences that need to be examined.

    There are option cards for the 890 series for LinkNET.  What region are you in?  Ideally we can get you in touch with your local Parker Authorized Industrial Drive Distributors, who can take a deeper look at what you need and suggest a solution for you.

    Regards,

    William

Reply
  • Ravi,

    The AC30 line does not support the firewire protocol.  For the AC30's in North America, we usually recommend LinkNET as the peer-to-peer communication between the drives.  There should not be any programming difference when using LinkNET, but there may be other differences that need to be examined.