Home Technologies Electromechanical Group Electromechanical - Industrial Electromechanical Industrial Knowledge Base Encoder Velocity
      • 9000 (Legacy)+
      • Encoder Velocity
      • Evaluation Underflow error
      • How to receive ASCII data
      • INTCAP
      • MFLOPS vs. MIPS
      • Reboot in startup program
      • Use of AXIS format
      • User Variables
      • Using Encoder 8 or 9 as SRC
      • What is the axis velocity
      • Axis Flag update rate
Encoder Velocity
The Encoder Velocity Parameter is encoder pulses per servo interrupt. The default value of servo interrupt is 500 uSec so this is usually a very small number.
If you are trying to calculate velocity, see the sample program below:
REM ********************************************
REM Program to determine speed of source encoder
REM Be sure to allocate 1000 bytes of memory for Program
HALT
NEW
DETACH
AXIS1 ON
ATTACH MASTER1
ATTACH SLAVE0 AXIS1 "Y"
10 DIM LV2
20 P1=0
30 P4=0
100 INTCAP Y0 :REM Trigger INTCAP on marker
110 INH 809 :REM Assign P2 to value of Hardware capture register
120 P2=P12548 :REM Assign P5 to the value of Global system clock
130 P5=P6916
170 P3=(P2-P1):REM Determine pulses between marker pulse
180 P6=(P5-P4):REM Determine time (ms) between marker pulse
190 LV0=((1000/P6)*60):REM Calculate RPM
200 PRINT "Encoder count = ";P3;" * Time in mSeconds = ";P6
210 PRINT "RPM = ";LV0
220 PRINT " "
300 P1=P2
310 P4=P5
390 GOTO 100
REM ***** LRUN program to display information *****
Related FAQ:  How Fast is Servo Axis Moving?