TCP/IP port: 44821
Turn all the switches on S24 off (left).
For 192.168.0.230, the object 860.3 (IP address) needs to be set to -1062731546
For the subnet of 255.255.255.0, the object 860.5 (Subnet mask) should be set to -256
Requires WF Write to Flash.
Requires cycling power.
192 dec = C0 HEX
168 dec = A8 HEX
0 dec = 00 HEX
230 dec = E6
C0A800E6
In Microsoft's calculator program click = and then +/-, it will give FFFF FFFF 3F57FF1A
Convert 3F57FF1A to decimal (1062731546) and add - in front of it.
Or subtract C0A80036 from FFFF FFFF FFFF FFFF and add 1,it will give FFFF FFFF 3F57FF1A
Convert 3F57FF1A to decimal (1062731546) and add - in front of it.
Note that object 860.3, 860.5, users must click WF in the bottom left of the Optimization screen to Write to Flash to retain after cycling power.
To see these objects in C3 ServoManager:
Type :ro860.3 or :ro860.5 in the bottom left of optimization screen.
Users can gain access to the Object Tree in the bottom right-hand window of the Optimization Screen:
How to View or Monitor any Object in Optimization (Activate Object Tree)
In the Online tab, it'll set the focus, so you don't need to do the :ro and object number, you can just set the value.
Do the WF to write to flash.
Make sure the dipswitches on S24 are all OFF (to the left).
Cycle power.
Then if you do an upload, in the Device selection > Online device identification, scroll down and you can see the IP address:
9/22/15jh updated with new object tree (rel 9-00 and higher)