Home Technologies Electromechanical Group Electromechanical - Industrial Electromechanical Industrial Knowledge Base P Series Drives - Indexer Version - Analog Inputs (command inputs) for Torque Control (or Velocity Control)
The P series drives can be configured for Torque Control or Velocity Control from a traditional +/- 10VDC analog input.
For Torque Control mode the analog input 1 is used (A-TLMT aka AI1) relative to AGND.
For Velocity Control mode the analog input 2 is used (A-OVR aka AI2) relative to AGND.
Refer to object 0x221C which is used to configure the analog input scaling for torque mode (or 0x229 for velocity mode).  For the torque mode operation, the default analog input scaling is for 100% of the motor's rated torque so if your application requires peak torque from the system you will need to change this scaling as appropriate for your motor's peak ratings (many motor's peak torque ratings are 3 times their rated torque so a value of 300 for object 0x221C may be appropriate for 10V input to equal your motor's peak torque rating).
These analog inputs also have functionality in Pulse/Indexer mode as torque or velocity limiting inputs.  See P series user guide for more details.
Important Note - The analog inputs on the P series drive are 12 bit resolution (ADC converters).  This is slightly lower than some other Parker torque or velocity control drives which offer 14 bit resolution inputs.  This generally will not affect your application unless driving a small motor requiring better torque resolution or a lower speed motor requiring better velocity resolution.
Torque Control Velocity Control Analog Input Analog Inputs Command Input Command Inputs analog resolution 14 bit resolution 12 bit resolution
glh 11/2015