Home Technologies Electromechanical Group Electromechanical - Industrial Electromechanical Industrial Knowledge Base How do I connect an AC10 to a TS8000?
  • AC/DC Industrial Drives-
    • AC10-
      • AC10 Heat Dissipation
    • AC15/AC20
    • DESAT (OVER I) Fault
Note that the TS8000 has been obsoleted.
The recommended software for TS8000 products is now DSI3. DSI8000 is referenced throughout this FAQ. DSI3 is available for download on the product page under "Product Support" on the TS8000 Product Page.
Despite many similarities, projects are not cross-compatible between DSI8000 and DSI3. This FAQ can still be utilized for wiring and setting up the AC10 to the TS8000. Necessary steps shown in DSI8000 are the same in DSI3, but overall window layout will be different.
Up to 31 AC10 drives can be connected to a Version 2 TS8000 HMI with Modbus RTU via RS485.
Equipment needed:This will require an AC10 drive, a TS8000 HMI and DSI3 software (or DSI8000 for an existing project) a USB cable, and a 124 ohm resistor.
There is a pre-configured TS8008 configuration example which corresponds to this application labeled 3855_TS8000_to_AC10_Modbus_8_inch.dsi. It is configured for 2, AC10 Drives communicating to a TS8008 HMI 8 inch screen.
NOTE: AC10 RS485 MODBUS communications to Version 1 TS8000 HMI is intermittent. It is recommended to use only Version 2 TS8000s.
Procedure
IMAGE BROKEN -- DCLIFFE
Wire the AC10 to the TS8000.
For RS485 2 wire connection, use an RJ45 connector from the RS485 terminal on the TS8000.
Pins 1 or 7 connect to the A terminal on the AC10 and terminals 2 or 8 connect to the B terminals on the AC10.
Note: It is required to have a 124 ohm resistor across the A and B terminals of the last drive in the network. Terminals A&B on the AC10 are swapped per the cables markings. Thus the drawing is correct.
Configure the AC10 Communication Parameters
Example Settings:
F900 (inverter address): 13 for Drive1 and 14 for Drive2.
F901 (Modbus mode selection): 2 (RTU mode)
F902 (Stop Bits): 1
F903 (Parity Check): 1 (Odd)
F904 (Baud Rate): 6 (57600)
Also:
F200 Source of Start Command = 3: Modbus or 4: Keypad + Terminal + Modbus
F201 Source of Stop Command = 3: Modbus or 4: Keypad + Terminal + Modbus
F203 Main Frequency Source = 10: Modbus
Configure the TS8000
Open DSI8000 or DSI3 and select the Communications window. This example was done with DSI. Select the RS485 port by clicking on the icon in the left hand pane. Then click 'Edit' in the top right-hand of the screen and select 'Modbus Master'.
Set the Baud Rate and Parity to match the settings in the drive.
Click on PLC1. Select the Drop Number box and enter the inverter address which matches the setting in parameter F900.
IMPORTANT: Click the Extended tab and select the ping holding register text box. The number in here must match a "parameter address" in the drive. Set the number in here to 262. This corresponds to parameter F105 Software Version "parameter address" location (The 262 comes from converting 105 (hex) to 261 +1).
AC10 Parameter Access via the TS8000
The parameters in the AC10 have to be converted into numbers that can be used in the Modbus registers.
Example: F111 (Max Frequency) the parameter number consists of 2 bytes.
01 + 11 Convert these into hexadecimal form to get 01 0B.
Convert this back to decimal and add 1. So 10B(h) = 267 + 1 = 268.
So the Modbus register = 400000 + 268 = 400268.
Set up the TS8000 Data Tags
Close the Communications window and double click on the Data Tags icon. Click on the data tags icon and create integer tags as shown. Name one as Speed and the other as Command. The speed tag will relate to the Target Frequency parameter F113.
F113 = 010Dh = 269 + 1 = 270.
Command is tag is F2000 = 8192 + 1 = 8193.
Set up the "User Interface"
Double click on the User Interface icon. Once the tags are created you can create an integer text box and configure it to enter the speed. The AC10 refers to the Speed in Hertz rather than a percentage as most other Parker drives do.
The value of the command tag sets the drive mode.
Run Forward = 0001
Run Reverse = 0002
Ramp Stop = 0003
Coast Stop = 0004
Create A button for each mode and set the integer value to match the function of the button.
If you are connected to the AC10 you can download it into the drive by pressing F9.
You should now be able to run the drive in both directions and Stop it with either a Ramped Stop or a Coast Stop. More parameters are listed in the AC10 product manual HA502320U001.
Note: If the AC10 drive is 'Faulted' communication to the TS8000 will be lost and dash lines will appear for the data values.
16NOV2016 LS
6SEP19 JD - Temporary DSI3 message. DSI3 update required in the future.
  • Modbus/RTU
  • TS8000
  • AC10
  • Modbus
  • DSI3