PDB IS NO LONGER SUPPORTED TO CONNECT TO THE AC10. IT WILL NOT WORK WITH MODERN FIRMWARE.
PLEASE UTILIZE DSELite FOR NEW APPLICATIONS.
UTILIZE THIS FAQ TO CONNECT WITH A GENERIC RS485 DEVICE VIA DSELite FAQ: RS485 with DSELite
UTILIZE THIS FAQ TO CONNECT WITH THE 1002-00 MODULE VIA DSELITE FAQ:1002-00 with DSELite
[QuickLink for the AC10 on Parker.com] - Manual, QuickStarts, Product Support, etc
Equipment Needed
AC10 drive, RS232 to RS485 converter, PDB.
Procedure
- Connect RS485 converter.
NOTE: The 120 Ohm resistor must be removed to work with PDB but must be in to work with TS8000 (HMI) communications. - Set up the computer's COM port.
- Set PDB protocol.
- Set AC10 protocol.
Parameter Description Setting Range Default F900 Communication Address 0: Broadcast Address
1-255: Single Inverter Address1 F901 Communication Mode 1: ASCII
2: RTU2 F902 *Stop Bits 0: None
1: 1 Stop Bit
2: 2 Stop Bits2 F903 Parity Check 0: Invalid
1: Odd
2: Even1 F904 Baud Rate (bps)
9600 is recommended0: 1200
1: 2400
2: 4800
3: 9600
4: 19200
5: 38400
6: 576003 F905 Communication Time Out 0-3000 0 *In the IP66 version, F902 is RESERVED
- AC10 Communication Settings
Mode = RTU
ASCII Mode Byte Function 1 Start Bit (Low Level) 7 Data Bit 0/1 Parity Check Bit (None for this bit in case of no checking. Otherwise 1 bit) 1/2 Stop Bit (1 bit in case of checking, otherwise 2 bits)
RTU Mode Byte Function 1 Start Bit (Low Level) 8 Data Bit 0/1 Parity Check Bit (None for this bit in case of no checking. Otherwise 1 bit) 1/2 Stop Bit (1 bit in case of checking, otherwise 2 bits)
Read Parameters, Write Commands, COM Parameters -- See Section 12 in AC10 Manual
PDB Program
Network Connection (2-wire)
3JAN2017 LS