Home Technologies Electromechanical Group Electromechanical - Industrial Electromechanical Industrial Knowledge Base Compax3 Hardware - Single Ended Step & Direction (I10T10
Single-Ended Input for Compax3
If the customer cannot provide a differential RS422 signal because he has only a single-ended open-collector signal then he has to use an external 332 ohm open-collector resistor for the RS422 input, the inverse RS422 input needs a voltage-divider circuit with 821ohm / 600ohm and a 100nF capacitor.
Duplicate the circuit below for Step and Direction.
Single-Ended Step & Direction Diagram
The RS422 inputs have bus termination, and we use that capacitor to have a constant potential on the Step- and Direction- signals.
Step
Component Value PIN PIN
Resistor 332 Ohm X11/5 X11/7
Resistor 821 Ohm X11/5 X11/6
Resistor 600 Ohm X11/6 X11/15
Capacitor 100nF X11/6 X11/15
Direction
Resistor 332 Ohm X11/5 X11/8
Resistor 821 Ohm X11/5 X11/12