How can you add a divisor from a MULTIPLIER block instance to the OPERATOR MENU (or a TS8000) in an AC890 configuration?
You cannot make a connection line to an operator menu block. Setpoints can only be added using a DECIMAL parameter number.
Select a parameter to be displayed in the Operator menu.
Enter the correct PREF on the Keypad OR Enter an equivalent decimal number when using LINK or comms link.
NOTE: To convert the required PREF to the decimal number, multiply the PREF whole number by 32. Then add the remainder of the PREF.
For example: PREF 111.08 is equivalent to 3560 ((111 x 32) + 8).
In the case of block instances, where the block does not have a parameter number, a parameter from an unused block (like the FLUXING block) can be used as a place holder.