Home Technologies Electromechanical Group Electromechanical - Industrial Electromechanical Industrial Knowledge Base Updated Control Terminal Torque Specifications for AC10 VFD’s
  • AC/DC Industrial Drives-
    • AC10-
      • AC10 Heat Dissipation
    • AC15/AC20+
    • DESAT (OVER I) Fault
It has been determined that the AC10 control terminal torque specification of 0.6Nm in the product manuals for both the IP20 and IP66 (NEMA4X) versions is incorrect. The correct control terminal torque specifications are as follows:
IP20 Version  P/N’s beginning 10G-
           Frame 1                         0.2Nm
           Frames 2 & larger          0.4Nm
IP66 (NEMA4X) Version  P/N’s beginning 16G-
            All Frames                     0.4Nm
glh 9/2020