Home Technologies Electromechanical Group Electromechanical - Industrial Electromechanical Industrial Knowledge Base AC10 Modbus-RTU Example to Interact Xpress HMI (XTA)
  • AC/DC Industrial Drives-
    • AC10-
      • AC10 Heat Dissipation
    • AC15/AC20
    • DESAT (OVER I) Fault
This example shows some basic data exchanges between a Parker AC10 VFD drive and a Parker Interact Xpress XT HMI over Modbus/RTU and an RS485 connection.
See the AC10 Installation Guide for more details on its Modbus/RTU implementation (Chapter 12):
AC10 IP20 User Guide
AC10 IP66 User Guide
The specific Modbus/RTU settings in the Xpress application are as follows to match up the AC10 defaults pretty closely.
The AC10 Modbus implementation limits 'block reads' to 10 registers or less.
Tag address list for the Xpress project:
Fullscreen Xpress_to_AC10_via_Modbus-RTU_Tags.txt Download
Name				 Address
OutputFrequency			 h401000
OutputVoltage			 h401001
OutputCurrent			 h401002
PoleNumbers_ControlMode	 	 h401003
BusVoltage			 h401004
DriveRatio_InverterStatus	 h401005
PercentOutputTorque		 h401006
InverterTemp			 h401007
ApplicationSelection		 h40021C
DI1Functions			 h400310
DI2Functions			 h400311
DITerminalStatus		 h40100B
TerminalOutputStatus		 h40100C
AI1Value			 h40100D
AI2Value			 h40100E
Motor_StatorResistance		 h400806
AO1Value			 h401015
AO2Value			 h401016
CurrentSpeed			 h401017
Motor_RotorResistance		 h400807
ControlValue			 h402000
DI3Functions			 h400312
DI4Functions			 h400313
DI5Functions			 h400314
DI6Functions			 h400315
DI7Functions			 h400316
DI8Functions			 h400317
Motor_AutotuneType		 h400800
Motor_RatedPower_kW		 h400801
Motor_RatedVoltage_V		 h400802
Motor_RatedCurrent_A		 h400803
Motor_NumberofMotorPoles	 h400804
Motor_RatedRotarySpeed_RPM	 h400805
Motor_RatedFrequency_Hz	 	 h40080A
TargetFrequency			 h40010D
DO1Functions			 h400301
DO2Functions			 h400302
FactoryReset			 h40013C
Motor_LeakageInductance	 	 h400808
Motor_MutualInductance		 h400809
RelayOutputFunctions		 h400300
DIActiveLevel			 h400328
AO1Functions			 h40041F
AO2Functions			 h400420
MainFrequencySource		 h400203
Example Xpress Manager project:
AC10 Modbus Example to Interact Xpress HMI.zip
glh     10/2021