Home Technologies Electromechanical Group Electromechanical - Industrial Electromechanical Industrial Knowledge Base Compax3 Accessories - PS or Option 5 wiring option to Compax3
The new PS wiring option for the SM, BE, Neometric and J Series motors and Option 5 for all MPM Series motors is the perferred cabling option for all ViX, Aries and Compax3 drives. Below are the pinouts of the cables to the Compax3 drives.
COMPAX3
Cable Part Numbers
Motor Series Motor Power Cable Encoder Feedback Cable Resolver Feedback Cable
SM16 / SM23 / N070 / N034 / J070 / J034 / BE16 / BE23 / MPM* 71-021626-XX 71-022231-XX 71-021629-XX
BE34 / N092 / J092 / MPM** 71-021627-XX 71-022231-XX 71-021629-XX
* All motors with 6 Arms continuous current or less.
** All motors with 20 Arms continuous current or less.
Motor Power Connections
Motor Pin # Drive Connection Function Wire Color
1 U Phase U Black 1
2 V Phase V Black 2
6 W Phase W Black 3
3 PE Earth Green/Yellow
4 BR*** Brake Red/Blue
5 BR*** Brake Red/Blue
*** See the Compax3 drive manual for specific brake connections.
Resolver or SinCos Connections
1 7 SIN -
2 8 SIN +
4 9 CLKfbk/
5 13 DATAfbk
6 14 DATAfbk/
7 6 CLKfbk
8 & 13 5 +5 VDC
9 10 Tmot
11 12 COS +
12 11 COS -
14 4 REFres +
17 15 REFres -
Encoder Connections
1 7 ENC A-
2 8 ENC A+
4 3 Hall 1
5 6 Hall 2
6 9 Hall 3
7 15 ENC GND
8 5 +5 VDC
9 10 Tmot
11 12 ENC B+
12 11 ENC B-
13 5 +5 VDC
15 13 ENC Z+
16 14 ENC Z-
Please note that BE 16 frame motors do not have the temperature switch implemented into the motor due to the smaller frame size.
When configuring an amplifier for a BE 16 frame motor, be sure to disable the thermal switch checking.