Home Technologies Electromechanical Group Electromechanical - Industrial Electromechanical Industrial Knowledge Base Gemini - MaxPlus (MPM) Encoder Option 1 Connection
The following is a table for the MaxPlus (MPM) Encoder Option 1 Termination to Gemini Connections:
Feedback Connections
Gemini Feedback ConnectorOption 1 Encoder Cable (175-0xxx)***
Wire FunctionPin#Pin LetterFunctionWire Color***
Encoder Ground3 or 4 TGNDBlack
Encoder +5VDC1 or 2K+5VDCRed
Encoder A+5BCH ABlue/White
Encoder A-6CCH A\Black/White
Encoder B+7NCH BBlue
Encoder B-8PCH B\Yellow
Encoder Z+9MCH ZYellow/White
Encoder Z-10UCH Z\Red/White
Hall A16ECH UPink
None*N.C.*RCH U\Tan
Hall B17FCH VWhite
None*N.C.*SCH U\Green
Hall C18GCH WBrown/White
None*N.C.*HCH W\Orange/White
Connector Housing****DGnd/CableDrain
Thermal Switch12ATHERMOrange
Thermal Switch13LTHERMBrown
Connector Housing****JSHLDBlack
*The Hall signals on the MPM motors are diffential, therefore, you do not need to connect the negative signals of each hall state to the single-ended Gemini Hall signals.
**The shield connections of the feedback cable should be connected to the Gemini Feedback header's metal housing (if possible).
***The wire colors may not apply to your cable. Option 1 encoder cable wire colors can vary, however, the wire function should be consistent among all cables. If your cable wire marker (labels) are no longer present or readable, please contact Parker.
Motor Power Connections
Gemini Motor Power Screw TerminalsOption 1 Motor Power Cable
FunctionPhasePin LetterFunctionWire Color
Phase UUAPhase RRed
Phase VVBPhase SBlack
Phase WWCPhase TBlue
GroundGNDDPE GNDGreen/Yellow
Hall Commutation Chart with MXPLUS1*
PhaseHall StateDirection
U TerminalV TerminalW Terminal#Clockwise**
+-+3|
+--2|
++-6|
-+-4|
-++5|
--+1V
*Please refer to Appendix B - Non-Compumotor Motors section of the Gemini GV/6/6K Hardware Installation Guide for further information.
This chart applies only if CMDDIR0, ENCPOL0, & SHALL0 (all defaults) are set properly. The encoder counts positive when the motor shaft rotates clockwise.
**Clockwise rotation with respect to the motor shaft extended towards the operator.
Notes:
MXPLUS command - For GV/GV6 you must have Gemini OS ver. 2.12 or greater. GV6 You must have ASCII translator ver. 1.46 or greater. For GV6K, you must have OS ver. 6.4.2 or greater. You must have Com6SRVR.exe ver. 3.3.2.4 or greater. Because the MaxPlus motor's commutation cycle is different than the legacy Compumotor series motors, the MXPLUS command compensates for this through software. It does the following: 1)Switches Hall Signals A and B, 2) Inverts the level of all the signals like SHALL1, 3) Inverts the commanded direction and encoder feedback polarity internally similar to CMDDIR1 (see Encoder Polarity below).
Encoder Polarity - the encoder will still count positive when the motor shaft rotates clockwise. However, the encoder output signals on the DRIVE I/O connector, pins 14 -19, will now count in the opposite direction. Therefore, a clockwise rotation of the shaft will increase encoder counts when TPE is queried on the drive, but will decrease the encoder counts sent out of the drive to an external device connected to DRIVE I/O.
6K Controller connection - the encoder output (DRIVE I/O pins 14-19) now counts opposite to a positive commanded input because of MXPLUS1, the encoder polarity on the 6K Controller MUST be set to invert, ENCPOL1, direction for each servo axis.
ACR Controller connection - the encoder output (DRIVE I/O pins 14-19) now counts opposite to a positive commanded input because of MXPLUS1, the encoder polarity on the ACR Controller MUST be set to invert, MULT to a negative value, direction for each servo axis.
DMODE13 (Autorun) - the motor turns counter-clockwise with MXPLUS1.