• Home
  • Investors
  • Contact Parker
  • Sign In / Register
Parker Community
  • Site
  • User
  • Site
  • Search
  • User
  • Products
  • Support
  • Divisions
  • Where to Buy
  • Careers
  • About Parker
Home Parker Community Technologies Electromechanical Group Electromechanical Knowledge Base Can the AC890 be used in an electronic lineshaft application?
Sign In / Register

Sign In

Register

  • Electromechanical Knowledge Base & Frequently Asked Questions
  • Motion and Machine Controllers+
  • General Technology Information+
  • Virtual Engineer+
  • Visualization and Human Machine Interface (HMI)+
  • Servo Drives and Servo Drive/Controllers+
  • Stepper Drives and Stepper Drive/Controller+
  • Gearheads+
  • AC and DC Drives and Inverters-
    • AC10+
    • AC30+
    • AC690+ Series+
    • AC890 Series-
      • What are the basic wiring connections for the AC890?
      • What software and communication cable are used for programming an AC890?
      • How to Install and Extract Parameters From a 890 or 890PX Drive Using DSE Lite?
      • 890 - Interact Xpress with the AC890
      • 890: Why am I getting over-voltage trips?
      • 890PX - Proper ethernet cable - Current Balance, Undervoltage, Missing Phase
      • Can I clone an 890 drive via the Keypad?
      • Can the AC890 be configured as an Active Front End (AFE)?
      • Can the AC890 be used in a load-sharing application?
      • Can the AC890 be used in an electronic lineshaft application?
      • Can the AC890 be used in an encoder following application?
      • Converting .001 file types to .prj file type
      • How can I get the DSE software?
      • How can I get the DSELite software?
      • How can I load different firmwares?
      • How can I recover from a COMMS CODE N error on the AC890
      • How can I troubleshoot Firewire problems?
      • How can the 890 family be configured?
      • How can the AC890 be reset to factory defaults?
      • How can you add an item to the OPERATOR MENU in an AC890?
      • How do I determine an 890 drive TAG NUMBER so it can be used in DSE890?
      • How do I know what firmware revision my AC890 is?
      • How do I make an 890 Phase move?
      • How do I startup & troubleshoot a PMAC motor on the 890?
      • Is the keypad detachable during operation?
      • Is there any additional information on troubleshooting 690+ and AC890 Frame K drives? (copy)
      • My 890 control board locked up when updating the firmware, how can I reset the control board?
      • The AC890 is enabled, and START is true, but the motor runs slow with high torque. Why?
      • The AC890's DC bus voltage is extremely high on power-up. Why?
      • The AC890PX DC bus voltage is extremely high on power up. Why?
      • What are the minimum and maximum 3-phase input voltage ratings on an 890SD, CD, CS and PX?
      • What are the reference power supplies available to terminal connections on the AC890?
      • What can I use to replace an 8902/RR/00/00?
      • What configurable I/O is available on the AC890?
      • What is the current overload rating for the AC890 drive?
      • What is the maximum operating altitude for the AC890?
      • What is the operating temperature for the AC890?
      • What kind of I/O is available on the AC890?
      • What options can be added to the AC890/890PX?
      • What safety standards does the 890 meet?
      • What slots I can put options in, and how do I install them?
      • What types of speed feedback are supported for the AC890?
      • Where do I find default configurations?
      • Why am I getting an Incompatible Power Board message?
      • Why can't I connect to my AC890 drive with the USB cable
      • Why is my AC motor running hot?
      • Why is the LED on the control board flashing 50% red and 50% green?
      • Why won't DIN3 stop my 890 drive with a default configuration in remote mode?
      • Why won't my AC890 inverter run my motor?
      • HOW DO I CONVERT AC890 UK/JDE PART NUMBERS TO US PART NUMBERS?
      • HOW DOES THE INVERSE TIME (OVERLOAD) FUNCTIONALITY PROTECT THE DRIVE (890)?
      • Runtime alert when connecting to or downloading a project to an 890 drive - DSEv3.10
    • DC590+ Series+
    • TS8000, DSI3, & DSI8000+
    • Legacy/Discontinued VFD Products+
    • What software and communication cable are used for programming?
    • DSE Lite and Drive Firmware Compatibility
    • How do I update my DSE, DSELite, DSI3, DSI8000, or DSD software?
    • How do I migrate my DSE (DSE890), DSELite, DSD software to a new computer?
    • Why does DSE or DSELite crash when creating or opening a new project?
    • How can I flash the LinkNet Techbox firmware?
    • What is an Autotune and how do I run one?
    • Do you have CAD available for SSD Products? AC10, AC30, 590+, 650 (OBX), 690+, 890
    • 6053...6054...6055...? Techbox options
    • How do I cross a Legacy or Parker European part number to modern Parker North American part numbers?
  • Servo Motors+
  • Step Motors+
  • Linear and Rotary Positioners+
  • Electric Cylinders+
  • T-Slot Aluminum Framing+
  • OEM Products+
  • C3 + Xpress + ETH+
  • How can I stay updated on Parker electromechanical and drives product news?
  • Legacy (Discontinued)+
  • Other+
  • Other Groups
    • Parker Indego
      • Parker Indego Instructors
      • Parker Indego Therapists
      • Parker Indego Distributors
  • Technologies
    • Aerospace
    • Climate Control
    • Electromechanical Group
      • Parker IPS Design Center Community
    • Filtration
    • Fluid and Gas Handling
    • Hydraulics
    • IoT
      • Mobile IoT
    • Pneumatics
    • Process Control
    • Sealing and Shielding
  • Blogs
  • Forums
  • Knowledge Base
  • Home
  • All Blogs
  • Home
  • Electromechanical Blog
  • Electromechanical Group Forums
  • Electromechanical Knowledge Base
  • Electromechanical Group Members
  • Mentions
  • Electromechanical Group Sub-Groups
  • Tags
Follow Us
  • Follow Parker Hannifin on social media

Follow Parker Hannifin on social media:

Can the AC890 be used in an electronic lineshaft application?

Print Friendly and PDF

AC890 Phase Control

To configure an AC890 drive for a Phase Lock application. In this example application, a Stand Alone 890 drive will follow an external Reference Encoder.

Equipment:

An 890 Drive operating in the Closed Loop Vector mode and the software DSELite or DSE890. An Encoder or Resolver must be mounted to the motor. An 8903/EP Encoder Option card (or 8903/AI) must be fitted in the drive. The drive must also be configured for Advance performance. A FireWire 8903/FA option card is not required in the drive.

Function Block Setup:

The following parameters must be changed from the default to perform a Phase Lock in the Master drive:

  1. In the COMMS CONTROL block set FIREWIRE REF SEL to True.
  2. In the VIRTUAL MASTER block set CHANNEL to 1 (or any channel but 0).
  3. In the VIRTUAL MASTER block set SOURCE to REFERENCE ENCODER.
  4. In the FIREWIRE REF block set CHANNEL to 1 (Channel must match step 2).
  5. In the POSITION LOOP block set ENABLE to True.

Set-Up Procedure:

  1. This application requires that a 8903/EP Encoder Option card (or 8903/AI ) be installed in the drive. This will be the Master Speed Reference that the drive will follow.
  2. Make sure that the drive has been Auto tuned and the drive is operating in the Closed Loop Vector mode.
  3. Using DSE set up the function blocks as described above. Enter the data for the Reference Encoder block. This is the external reference encoder that the drive will follow. Usually only the Encoder Lines will have to be entered.
  4. In the FireWire Ref block Gear A & Gear B may have to be calculated. If The Gear A / Gear B is set to 1/1, the Slave drive will follow the Master Reference Encoder exactly at 1:1 speed.
  5. If the speed is different these parameters need to be set up. For an example, if the Master Encoder had a max speed of 3500 rpm, and the slave encoder has a Max Speed is 1800, set Gear A to 100000, and Gear B to 194444 to give 3500/1800 = 1.944444. This will gave a 1 to1 rpm speed match.

Additional Information:

If the Slave drive needs to go reverse, set the Gear Ratio A or B to a negative number. In the Comms Control block, the FireWire Ref Select was set to True to use the Fire Wire Reference. This could be switched false to do an individual jog or other function if needed.

If a Rapid Traverse function is needed, the Phase Inch block can be used. When Adv or Rtd are selected, the block adds or subtracts counts in revolutions to the master position commanding the slave to speed up or slow down. The default rate scale of 1 and a maximum rate of 30 (which is the max value). If more counts are needed the Rate Scale can be used. This will have the drive increase/decrease at a very large rate.

BROKEN IMAGE -- DCLIFFE

Objective:

In this example application, 890 drives will be configured to obtain a Phase Lock application between a Master and Slave Drives.

Equipment:

An 890 Drive operating in the Closed Loop Vector mode and the development software DSE890. A feedback device must be mounted on the motors. The FireWire option cards are also required on the drives.

Function Block Setup for the Master Drive:

The following parameters must be changed from the default to perform a Phase Lock in the Master drive:

  1. In the VIRTUAL MASTER block set CHANNEL to 1 (or any channel but 0). This is the Firewire broadcast channel, in which the drives will obtain their Speed Reference.
  2. In the VIRTUAL MASTER block select the SOURCE to FEEDBACK POSN for Feedback Position. The SOURCE has a selection of:

     

    1. S RAMP the Virtual Master Output is derived from the INPUT parameter via an sramp function.
    2. FEEDBACK POSN the Virtual Master Output is the motor shaft speed and position, unchanged. Thus the Speed Command is derived from the REFERENCE block.
    3. REFERENCE ENCODER the Virtual Master Output is the reference encoder speed and position, unchanged. Thus a Reference Encoder option card is required in Slot A.
    4. LINEAR RAMP the Virtual Master Output is derived from the INPUT parameter, passed through a linear ramp function.

Function Block Setup for the Slave Drive

The following parameters must be changed from the default to perform a Phase Lock in the Slave drive:

  1. In the COMMS CONTROL block set FIREWIRE REF SEL to True.
  2. In the FIREWIRE REF block set CHANNEL to match the Master Drive CHANNEL. (In this example it is CHANNEL 1.)
  3. In the POSITION LOOP block set ENABLE to True.

Setup Procedure:

  1. Using DSE890 set up the function blocks as described above for the MASTER drive. Select the SOURCE type to one of the 4 options described.
  2. Using DSE890 set up the function blocks as described above and shown on Sheet 4, for the SLAVE drive.
  3. Make sure that the drive has been Auto tuned and the drive is operating in the Closed Loop Vector mode.

Master Drive: Setup if SOURCE is FEEDBACK POSN

BROKEN IMAGE -- DCLIFFE

The Speed Demand is derived from the Reference block.

Master Drive: Setup if SOURCE is S RAMP

BROKEN IMAGE -- DCLIFFE

Master Drive: Setup if SOURCE is LINEAR RAMP

BROKEN IMAGE -- DCLIFFE

Master Drive: Setup if SOURCE is REFERENCE ENCODER

BROKEN IMAGE -- DCLIFFE



BROKEN IMAGE -- DCLIFFE

[QuickLink for the 890 on Parker.com] - Manual, QuickStarts, Product Support, etc

8NOV2016 LS

  • lineshaft
  • electronic
  • 890
  • Share
  • History
  • More
  • Cancel
Related
  • Other Groups
    • Parker Indego
      • Parker Indego Instructors
      • Parker Indego Therapists
      • Parker Indego Distributors
  • Technologies
    • Aerospace
    • Climate Control
    • Electromechanical Group
      • Parker IPS Design Center Community
    • Filtration
    • Fluid and Gas Handling
    • Hydraulics
    • IoT
      • Mobile IoT
    • Pneumatics
    • Process Control
    • Sealing and Shielding
  • Home
  • All Blogs
  • Home
  • Electromechanical Blog
  • Electromechanical Group Forums
  • Electromechanical Knowledge Base
  • Electromechanical Group Members
  • Mentions
  • Electromechanical Group Sub-Groups
  • Tags
Follow Us
  • Follow Parker Hannifin on social media

Follow Parker Hannifin on social media:

Parker Hannifin Parker Hannifin

  • Products
  • About Parker
  • Investors
  • Community
  • Careers

Global Operations Global Operations

  • Divisions
  • Sales Companies
  • Worldwide Locations
  • Distribution Network
  • ParkerStoreā„¢ Network

Company Information Company Information

  • Newsroom
  • Event Calendar
  • Working with Parker
  • Product Brands
  • History

Global Support Center Global Support Center

  • Support
  • CAD
  • Where to Buy
  • Contact Parker
  • Manage Online Orders
Parker - Engineering Your Success
  • Site Map
  • Safety
  • Privacy Policies
  • Terms and Conditions
Ā© Parker Hannifin Corp 2021